AFF A250 / FAS500f Low Bat_Dstg_Cycles cause BATTERY (capacity low) error
Applies to
- AFF A250
- FAS500f
- NVRAM battery firmware C0 or lower
BMC node_name> system battery show
DeviceChemistry : LION
ChemistryID : 0x1968
DeviceName : bq40z50-R2
ManufacturerName : Inv27100073+C0
FW version : C0
Issue
- Events with
1/1/2022 00:00:00 node-name ALERT callhome.battery.low: Call home for BATTERY_LOW.
1/1/2022 00:00:00 node-name EMERGENCY monitor.nvramLowBattery: NVRAM battery is dangerously low.
1/1/2022 00:00:00 node-name ALERT callhome.battery.warning: Call home for BATTERY (capacity low) WARNING.
- EMS message with the error and correction (normal) reported
[node_name: env_mgr: nvmem.battery.capLowWarn:error]: The NVMEM battery capacity is below normal (5 cycles).
[node_name: env_mgr: callhome.battery.notice:notice]: Call home for BATTERY (capacity low) NOTICE.
[node_name: env_mgr: nvmem.battery.capNormal:notice]: The NVMEM battery capacity is normal.
- BMC event for low battery
123 | 06/16/2022 | 16:56:09 | Battery #0x49 | Lower Non-critical going low
system sensors show
reportsBat_Dstg_Cycles
is lower than or equal tolnc
=================== sensor ==========================
Sensor name | reading | unit | status| lnr | lcr | lnc | unc | ucr | unr
Bat_Temp | 34.500 | degrees C | ok | 0.000 | 0.000 | 5.000 | 60.000 | 75.000 | 127.500
Bat_Volt | 8.100 | Volts | ok | 0.000 | 5.500 | 5.600 | 8.500 | 8.600 | 12.750
Bat_Curr | 0.000 | Amps | ok | na | na | na | 1.200 | 1.520 | 2.540
Bat_Rem_Cap | 9.840 | Watts * hour | ok | na | na | na | na | na | na
Bat_Full_Cap | 10.800 | Watts * hour | ok | na | na | na | na | na | na
Bat_Charge_Curr | 0.000 | Amps | ok | na | na | na | 2.200 | 2.300 | 5.100
Bat_Charge_Volt | 8.200 | Volts | ok | na | na | na | 8.900 | 9.000 | 12.750
Bat_Design_Cap | 18.400 | Watts * hour | ok | na | na | na | na | na | na
Bat_Initial_Fcc | 20.400 | Watts * hour | ok | na | na | na | na | na | na
Bat_Dstg_Cycles | 4.000 | cycles | nc | na | 2.000 | 5.000 | na | na | na
Bat_Cycle_Cnt | 0.000 | cycles | ok | na | na | na | na | na | na
Bat_Power_Fault | 0x0 | discrete | 0x0180| na | na | na | na | na | na
Bat_Dsg_FET_Flt | 0x0 | discrete | 0x0280| na | na | na | na | na | na
Bat_Chg_FET_Flt | 0x0 | discrete | 0x0280| na | na | na | na | na | na
Bat_Pack_Invalid | 0x0 | discrete | 0x0180| na | na | na | na | na | na
Bat_Lrn_Active | 0x0 | discrete | 0x0180| na | na | na | na | na | na
- you excluded the false-positive NVMEM battery alerts option as described in: AFF-A250 reporting BATTERY (capacity low) alert and Bug 1447722
- Monitoring
EMS.log
forThe NVMEM battery capacity is below normal
at the end of the message we can see(# cycles)
- The cycles number dropped below 5
- Note: When cycles number Remain as 5, the battery should recover within one hour and no additional actions are necessary.