AFF A700 shuts down due to Environmental Reason Shutdown (Battery not present)
Applies to
- AFF A700
- FAS9000
- de-stage controller power module (DCPM), which contains the NVRAM10 battery
Issue
- System shuts down due to battery error
- From EMS:
Jan 21 01:45:15 [node-01:callhome.battery.failure:EMERGENCY]: Call home for BATTERY (not present) CRITICAL. Fri Jan 21 09:45:32 GMT [nvram.hw.initWarn:WARNING]: NVRAM hardware initialization: Failed to get Battery FRU info. Jan 21 01:46:20 [node-01:nvram.battery.not.present:EMERGENCY]: The NVRAM battery is not present. To prevent data loss, the system will shut down in 5 minutes. Jan 21 01:51:20 [node-01:monitor.shutdown.emergency:EMERGENCY]: Emergency shutdown: Environmental Reason Shutdown (Battery not present) Terminated . Uptime: 169d11h5m58s System powering down...
- From
system sensors show
from the Service Processor:
DCPM:
Bat_Status | 0x0 | discrete | Absent | na | na | na | na
Bat_Ambient_1 | na | degrees C | na | 0.000 | 3.000 | 47.000 | 52.000
Bat_Ambient_2 | na | degrees C | na | 0.000 | 3.000 | 47.000 | 52.000
Bat_Charge_Curr | na | Amps | na | na | na | 5.500 | 6.000
Bat_Charge_Volt | na | Volts | na | na | na | 8.350 | 8.400
Bat_Curr | na | Amps | na | -0.100 | -0.050 | 2.500 | 3.000
Bat_Cycle_Count | na | cycles | na | na | na | na | na
Bat_Design_Cap | na | Amps*hour | na | 0.000 | 0.000 | 6.375 | 6.375
Bat_Dstg_Cycles | na | cycles | na | 2.000 | 5.000 | na | na
Bat_Full_Cap | na | Amps*hour | na | 2.000 | 2.200 | 4.750 | 5.000
Bat_Initial_Fcc | na | Amps*hour | na | 2.000 | 2.200 | 4.750 | 5.000
Bat_Rem_Cap | na | Amps*hour | na | 0.250 | 0.500 | 4.750 | 5.000
Bat_Temp | na | degrees C | na | -5.000 | 0.000 | 55.000 | 60.000
Bat_Volt | na | Volts | na | 6.000 | 6.500 | 8.300 | 8.500
- From
events all
SP node-01> events all Record 1: Fri Jan 21 11:12:07.966816 2022 [SP.notice]: No response from battery charger Record 2: Fri Jan 21 11:12:08.142235 2022 [SP.notice]: No response from battery charger Record 3: Fri Jan 21 11:12:08.421014 2022 [SP.notice]: No response from battery charger Record 4: Fri Jan 21 11:12:08.538567 2022 [SP.notice]: No response from battery charger Record 5: Fri Jan 21 11:12:08.703007 2022 [SP.notice]: No response from battery charger Record 6: Fri Jan 21 11:12:08.918484 2022 [SP.notice]: No response from battery charger Record 7: Fri Jan 21 11:12:09.097875 2022 [SP.notice]: No response from battery charger Record 8: Fri Jan 21 11:12:09.314864 2022 [SP.notice]: No response from battery charger Record 9: Fri Jan 21 11:12:09.486175 2022 [SP.notice]: No response from battery charger