NetApp Knowledge Base
E-Series Controller cache battery failed - AutoSupport Message
1,530
Visibility:
Votes:
1
Category:
e-series-systems
Specialty:
esg
Last Updated:
Applies to
NetApp E-Series
Event Summary
SANtricity reports a FAILED_BATTERY-Recovery Failure Type Code: 6 in the Recovery GURU.
Validate
  • RECOVERY-GURU-PROCEDURES file shows failure entry of FAILED_BATTERY-Recovery Failure Type Code: 6.
  • MAJOR-EVENT-LOG file shows Controller cache battery failed, Event Type 210C.
  • TRAYS section in STORAGE-ARRAY-PROFILE file shows Battery status as Failed.
Example:
         Battery status:              Failed
         Age:                         1,825 days
         Days until replacement:      Not applicable
         Last learn cycle:            2021/01/21
         Next learn cycle:            2021/03/18
         Weeks between learn cycles:  8
         Part number:                 PN 36540-06
         Serial number:               <SERIAL NUMBER>
         Vendor:                      VN LSI
         Date of manufacture:         2015/07/01
  • bidShow(255,0,0,0,0,0,0,0,0,0) command output in STATE-CAPTURE-DATA file provides additional details about the battery failure including its safety status. Example below shows the battery under voltage safety status was triggered leading to its failure.
    • CUV: Cell Under voltage
    • CUVC: Cell Under voltage
    • COV: Cell Overvoltage
    • OCC#: Overcurrent In Charge #
    • OCC: Overcurrent In Charge Recovery
    • OCD#: Overcurrent In Discharge #
    • OCD: Overcurrent In Discharge Recovery
    • AOLD: Overload in Discharge
    • ASCC: Short Circuit In Charge
    • ASCD: Short Circuit in Discharge
    • OTC: Over temperature in Charge
    • OTD: Over temperature in Discharge
    • UTC: Under Temperature in Charge
    • UTD: Under Temperature in Discharge
SafetyStatus:          0x00000001 [ CUV ]
Resolution
  1. Any BBU failure must first be evaluated to ensure the current controller code is running before replacement.​​​​​ Especially for the following major releases:
  • 08.20.XX.XX - Must be 08.20.27.00 or greater
  • 08.25.XX.XX - Must be 08.25.14.00 or greater.
  • 08.30.XX.XX - Must be 08.30.50.01 or greater.
  • 08.40.XX.XX - Must be 08.40.60.01 or greater.
  • All other releases by the platform can be verified in the SANtricity Support Matrix
2. If the controller firmware is not current as listed above, the firmware must be updated first.
3. After the firmware is updated, a new manual learn cycle must be run - How to manually start a battery learn cycle using SANtricity
4. On rare occasions, this may need to be run twice to fully recover a battery affected by previous downrev code issues.
New to NetApp?
Scan to view the article on your device